SO Cord Ampacity and Termination Temp per 110.14(C)

Status
Not open for further replies.
My assumption is that you can use any temperature termination and that would change the value in the table. I guess that would assume 60C. Just a guess
 
3-phase busway tap-off box drop cords in 40C ambient.
If load <=100A on drop cord w/ 75C lugs

Using T310.16 @ 30C ambient:
#3cu @ 75C max = 100A

Using T310.15B1 for 40C ambient:
#2cu is 115*0.88 = 101.2A

Using equation 310.15(B):
#2cu = 115*Sqrt((75-40)/(75-30)) = 101.4A
 
Table 400.5(A)(1) for SO, SOW, SOO, SOOW etc cord, however, does not have temperature columns - I guess it assumes that all SO is 90C? So how is one supposed to verify compliance with 110.14(C)?
Annex B, Table B.2(1) appears designed for your multi-conductor cable in free air

Using equation 310.15(B) for 40C ambient:
#2cu = 105*Sqrt((75-40)/(75-30)) = 92.6A
 