Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Friday at 4:43 PM #21 My assumption is that you can use any temperature termination and that would change the value in the table. I guess that would assume 60C. Just a guess
My assumption is that you can use any temperature termination and that would change the value in the table. I guess that would assume 60C. Just a guess
R ramsy NoFixNoPay Electric Location LA basin, CA Occupation Service Electrician 2020 NEC Friday at 9:55 PM #22 JuliaTruchsess said: 3-phase busway tap-off box drop cords in 40C ambient. Click to expand... If load <=100A on drop cord w/ 75C lugs Using T310.16 @ 30C ambient: #3cu @ 75C max = 100A Using T310.15B1 for 40C ambient: #2cu is 115*0.88 = 101.2A Using equation 310.15(B): #2cu = 115*Sqrt((75-40)/(75-30)) = 101.4A
JuliaTruchsess said: 3-phase busway tap-off box drop cords in 40C ambient. Click to expand... If load <=100A on drop cord w/ 75C lugs Using T310.16 @ 30C ambient: #3cu @ 75C max = 100A Using T310.15B1 for 40C ambient: #2cu is 115*0.88 = 101.2A Using equation 310.15(B): #2cu = 115*Sqrt((75-40)/(75-30)) = 101.4A