chevyx92
Senior Member
- Location
- VA BCH, VA
Am I doing anything wrong when I have a load of 22.4 amps, 4 wire 208 volt that is cord and plug connected and I select #8 from table 400.5(A) column "A" which is good for 35 amps to size my cord? The load connected has 2 hots neutral and ground, fed from 3 phase panel. So I choose column A here because there are 3 ccc's. Right? If sized properly then why would the 30 amp 4 wire 250v male plug give me so much trouble getting the #8 in? Am I doing something wrong here?