S Stevenfyeager Senior Member Location United States, Indiana Occupation electrical contractor Nov 12, 2021 #1 I am buying #4 SOOW cord. Where in NEC is the amp rating ? I think # 6 has 50 amp rating. ………….Thanks
I am buying #4 SOOW cord. Where in NEC is the amp rating ? I think # 6 has 50 amp rating. ………….Thanks
O oldsparky52 Senior Member Location Wilmington, NC USA Nov 12, 2021 #3 Watch out for conflicts with 110.14(C)
G GoldDigger Moderator Staff member Location Placerville, CA, USA Occupation Retired PV System Designer Nov 12, 2021 #4 A typcal prefabricated SO cord will have a table of allowed amps versus length which is limited by the voltage drop at the load. And be sure to uncoil the cord before using.
A typcal prefabricated SO cord will have a table of allowed amps versus length which is limited by the voltage drop at the load. And be sure to uncoil the cord before using.
S Stevenfyeager Senior Member Location United States, Indiana Occupation electrical contractor Nov 12, 2021 #5 Thank you.