This thread appears to be about expediency and not about the NEC requirements
It appears that splices must be accessible. It appears that splices can be made in direct burial and Concealed Knob and Tube as the only exceptions.
300.13 Mechanical and Electrical Continuity ? Conductors.
(A) General. Conductors in raceways shall be continuous between outlets, boxes, devices, and so forth. there shall be no splice or tap within a raceway unless permitted by 300.15; 368.56(a); 376.56; 378.56; 384.56; 386.56; 388.56; or 390.7.
300.15 Boxes, Conduit Bodies, or Fittings ?Where Required. A box shall be installed at each outlet and switch point for concealed knob-and-tube wiring. Fittings and connectors shall be used only with the specific wiring methods for which they are designed and listed. Where the wiring method is conduit, tubing, Type AC cable, Type MC cable, Type MI cable, nonmetallic-sheathed cable, or other cables, a box or conduit body shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A) through (L).
(A) Wiring Methods with Interior Access. A box or conduit body shall not be required for each splice, junction, switch, pull, termination, or outlet points in wiring methods with removable covers, such as wireways, multioutlet assemblies, auxiliary gutters, and surface raceways. The covers shall be accessible after installation.
(B) Equipment. An integral junction box or wiring compartment as part of approved equipment shall be permitted in lieu of a box.
(C) Protection. A box or conduit body shall not be required where cables enter or exit from conduit or tubing that is used to provide cable support or protection against physical damage. A fitting shall be provided on the end(s) of the conduit or tubing to protect the cable from abrasion.
(D) Type MI Cable. A box or conduit body shall not be required where accessible fittings are used for straight-through splices in mineral-insulated metal-sheathed cable.
(E) Integral Enclosure. A wiring device with integral enclosure identified for the use, having brackets that securely fasten the device to walls or ceilings of conventional onsite frame construction, for use with nonmetallic-sheathed cable, shall be permitted in lieu of a box or conduit body.
Informational Note: See 334.30(C); 545.10; 550.15(I); 551.47(E), Exception No. 1; and 552.48(E), Exception No. 1.
(F) Fitting. A fitting identified for the use shall be permitted in lieu of a box or conduit body where conductors are not spliced or terminated within the fitting. The fitting shall be accessible after installation.
(G) Direct-Buried Conductors. As permitted in 300.5(E), a box or conduit body shall not be required for splices and taps in direct-buried conductors and cables.
(H) Insulated Devices. As permitted in 334.40(B), a box or conduit body shall not be required for insulated devices supplied by nonmetallic-sheathed cable.
(I) Enclosures. A box or conduit body shall not be required where a splice, switch, terminal, or pull point is in a cabinet or cutout box, in an enclosure for a switch or overcurrent device
as permitted in 312.8, in a motor controller as permitted in 430.10(A), or in a motor control center.
(J) Luminaires. A box or conduit body shall not be required where a luminaire is used as a raceway as permitted in 410.64.
(K) Embedded. A box or conduit body shall not be required for splices where conductors are embedded as permitted in 424.40, 424.41(D), 426.22(B), 426.24(A), and 427.19(A).
(L) Manholes and Handhole Enclosures. A box or conduit body shall not be required for conductors in manholes or handhole enclosures, except where connecting to electrical equipment. The installation shall comply with the provisions of Part V of Article 110 for manholes, and 314.30
for handhole enclosures.
IMC, RMC, FMC, LFMC, PVC, HDPE, NUCC, RTRC, LNFC, EMT, FMT, ENT
3xx.56 Splices and Taps. Splices and taps shall be made in accordance with 300.15.
CCFR
372.12 Splices and Taps. Splices and taps shall be made only in header access units or junction boxes. A continuous unbroken conductor connecting the individual outlets is not a splice or tap.
CMFR
374.6 Splices and Taps. Splices and taps shall be made only in header access units or junction boxes.
For the purposes of this section, so-called loop wiring (continuous unbroken conductor connecting the individual outlets) shall not be considered to be a splice or tap.
NE
382.56 Splices and Taps. Extensions shall consist of a continuous unbroken length of the assembly, without splices, and without exposed conductors between fittings, connectors, or
devices. Taps shall be permitted where approved fittings completely covering the tap connections are used. Aerial cable and its tap connectors shall be provided with an approved means for polarization. Receptacle-type tap connectors shall be of the locking type.
UFR
390.7 Splices and Taps. Splices and taps shall be made only in junction boxes. For the purposes of this section, so-called loop wiring (continuous, unbroken conductor connecting the individual
Exception: Splices and taps shall be permitted in trenchtype flush raceway having a removable cover that is accessible after installation. The conductors, including splices and taps, shall not fill more than 75 percent of the raceway area at that point.
CT
392.56 Cable Splices. Cable splices made and insulated by approved methods shall be permitted to be located within a cable tray, provided they are accessible. Splices shall be permitted to project above the side rails where not subject to physical damage.
CKT
394.56 Splices and Taps. Splices shall be soldered unless approved splicing devices are used. In-line or strain splices shall not be used.
M
396.56 Conductor Splices and Taps. Conductor splices and taps made and insulated by approved methods shall be permitted in messenger-supported wiring.