I posted couple weeks ago. If this sounds familiar because it is I posted about a 100hp 480v 112amps 3ph rotatory pump draws water from a reserve tank to a wash plant tank that also has a large HP tank for washing sand. The 100hp pump is a secondary pump to the primary pump at wash plant. The 100hp pump sits within 50' of primary and breaker trips still. The breaker is 150a magtrip turned up all the way and still trips.
You guys did list a couple options for the problem. Soft start, VFD or Flow valve. I was wondering what is need to size both the vfd and SOft start also If a flow valve is used would it be installed before or after the pump? I wish i could down load the pics but that never seems to work for me so I am limited with info sharing. I will provide as much info as I can on the problem. I believe the pump is to large for application and a hammering effect is causing the breaker to trip.
You guys did list a couple options for the problem. Soft start, VFD or Flow valve. I was wondering what is need to size both the vfd and SOft start also If a flow valve is used would it be installed before or after the pump? I wish i could down load the pics but that never seems to work for me so I am limited with info sharing. I will provide as much info as I can on the problem. I believe the pump is to large for application and a hammering effect is causing the breaker to trip.