Slight correction... breaker COULD be up to 250%. The only thing stopping you from using a smaller breaker is the risk of nuisance tripping. VFD = no inrush, no nuisance tripping.430.52 breaker should be 250% ...
Another slight correction to an earlier comment; I never recommend selecting a VFD based on HP alone, because motor FLA varies a lot between motors, especially as pole count increases. I always recommend buying VFDs and Soft Starters using your motor nameplate FLA. You can’t go wrong that way. I did a project a few years ago where the user bought qty 6, 250HP 480V VFDs in advance to get it in the budget, but it turned out the pumps had 250HP 12 pole motors, and the FLA was 366A, “250HP” VFDs were rated for 302A. Oops... restocking charges were reduced but still painful.