ptonsparky
Tom
- Occupation
- EC - retired
I have a 3 phase reactor rated at 8 amps on my shelf.
I have a 1.5 HP 1Ph motor, but not a load for it. FLA: 8.6 @ 230
Fluke 43B on the inrush average of three starts:
No Reactor: 83 amps With Reactor: 82.6 amps
Run NR: 6.13 Run WR: 5,38
VD across the loaded reactor 9.6 volts. (246.2 - 236.6)
Fluke 337 One Sample each time
Inrush NR: 36.6 WR: 36.7
Max: 28.1 WR: 27
37.5 KVA POCO transformer with about 100 foot lateral to 150 Amp service. Pretty stiff.
OPs MMV.
Totally scientific.
I have a 1.5 HP 1Ph motor, but not a load for it. FLA: 8.6 @ 230
Fluke 43B on the inrush average of three starts:
No Reactor: 83 amps With Reactor: 82.6 amps
Run NR: 6.13 Run WR: 5,38
VD across the loaded reactor 9.6 volts. (246.2 - 236.6)
Fluke 337 One Sample each time
Inrush NR: 36.6 WR: 36.7
Max: 28.1 WR: 27
37.5 KVA POCO transformer with about 100 foot lateral to 150 Amp service. Pretty stiff.
OPs MMV.
Totally scientific.