You could add a 200A SUSE enclosed circuit breaker in between the meter and your existing main panel. That circuit breaker becomes the service disconnect and overcurrent device and the only place with a neutral-ground bond. Ideally the load side has double lugs.
Then you run a 200A feeder to your existing main panel from one set of the lugs on the service disconnect. From the other set of lugs you run a 100A feeder tap to your 100A fused PV disconnect. You have a feeder interconnection instead of a supply side interconnection.
Now the 100A feeder for the bypass can run from the main panel to the manual transfer switch through the new service disconnect, the PV disconnect, and the Sol-Ark inverter. Ideally each of those cabinets would be within 24" of conduit run from its neighbors, so that no derating is required.
Cheers, Wayne
Then you run a 200A feeder to your existing main panel from one set of the lugs on the service disconnect. From the other set of lugs you run a 100A feeder tap to your 100A fused PV disconnect. You have a feeder interconnection instead of a supply side interconnection.
Now the 100A feeder for the bypass can run from the main panel to the manual transfer switch through the new service disconnect, the PV disconnect, and the Sol-Ark inverter. Ideally each of those cabinets would be within 24" of conduit run from its neighbors, so that no derating is required.
Cheers, Wayne