Sol ark installs vs 690.31

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
Any idea what they think the issue is or could be?
If there is a fault there is a concern that the peanut butter will mix with the chocolate. We don't want DC on the AC conductors and vice versa in the event of a cross conductor fault since the protection system have different ratings.
 
If there is a fault there is a concern that the peanut butter will mix with the chocolate. We don't want DC on the AC conductors and vice versa in the event of a cross conductor fault since the protection system have different ratings.
I don't find that argument to make any sense. Couldn't the same thing be said of AC+AC conductors? Say small and large AC conductors in the same conduit or raceway or box? I could have some 12 gauge conductors in a circuit with some big feeder conductors and there's no restriction, and if there is a cross fault that big circuit could turn those 12 gauge conductors into chowder.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
25 years ago high current and voltage DC was not so much a thing as it is now with the proliferation of PV systems. Some AHJs I have worked with say no AC and DC in the same raceway or gutter, no matter what.
Even if the DC is non-PV? You certainly seem to work with more AHJs that ignore what the code explicitly permit than most do.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I don't find that argument to make any sense. Couldn't the same thing be said of AC+AC conductors? Say small and large AC conductors in the same conduit or raceway or box? I could have some 12 gauge conductors in a circuit with some big feeder conductors and there's no restriction, and if there is a cross fault that big circuit could turn those 12 gauge conductors into chowder.
Yeah I don't really see the reason to allow 600V AC in the same conduit as 120V AC circuits, but not 600V DC. Either of the 600V sources is going to wreak a lot of havoc if it gets onto the 120V circuit.
 