uwireme

Member
Location
Cottonwood, CA
I will be upgrading a electrical service from 100 amps to 200 amps. I typically install a mechanical interlock from the main breaker to a 2 pole backup generator breaker in the main service panel and install a outlet for a portable back up generator. This is the first time there are solar panels installed. Is there a way to do this with only one panel or will I have to put in a sub panel for the generator? I am not a solar guy...the solar is tapped off the load side of the main 100 amp breaker then going to a 30 amp fused disconnect switch so my thought was just put the feed for the solar to a 30 amp breaker and install labels. What do you think?
 
I will be upgrading a electrical service from 100 amps to 200 amps. I typically install a mechanical interlock from the main breaker to a 2 pole backup generator breaker in the main service panel and install a outlet for a portable back up generator. This is the first time there are solar panels installed. Is there a way to do this with only one panel or will I have to put in a sub panel for the generator? I am not a solar guy...the solar is tapped off the load side of the main 100 amp breaker then going to a 30 amp fused disconnect switch so my thought was just put the feed for the solar to a 30 amp breaker and install labels. What do you think?

If you are redoing the electrical service anyway, it would be easy to change to a line side connection. Just install a wireway or box after the meter and tap of to a fused disconnect for the PV. Another way to do it is use a 320 socket then you get your 2nd set of lugs for the PV. Obviously check utility requirements and get their approval. I have to say that I have a hard time believing that a cheap consumer generator wont be nearly instantly rejected by the inverter, but obviously as pro's we cant assume that.
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
I will be upgrading a electrical service from 100 amps to 200 amps. I typically install a mechanical interlock from the main breaker to a 2 pole backup generator breaker in the main service panel and install a outlet for a portable back up generator. This is the first time there are solar panels installed. Is there a way to do this with only one panel or will I have to put in a sub panel for the generator? I am not a solar guy...the solar is tapped off the load side of the main 100 amp breaker then going to a 30 amp fused disconnect switch so my thought was just put the feed for the solar to a 30 amp breaker and install labels. What do you think?

Move the solar to a supply side interconnection on the grid side of the ATS and do what you normally do with the generator.
 