The garage is heated at 50 degrees,it's lithium iron phosphate not lythium ion,(upgrade from company 10 year warranty,it's for the whole house and the garage,grid tie adds contracts and extra cost for epuipment i don't want or need.
Lithium batteries no matter the chemistry, can't be charged at cold temperatures. The OP stated the garage was not normally heated. I looked at this kit, and at the EG4 electronics website. I could be wrong, but it looks shady to me. Their standard inverter warranty is 5 yrs, prorated to reduce by 1/4 per year if replacement needed. Similar 5yr warranty on the battery with same proration. I don't see any evidence they meet any of the IEEE or other standards that most common inverters and ESS meet. More common manufacturers do not have this prorated warranty and generally it is common to have 10-12yrs on the inverter and 10yrs on the ESS. Also, a warranty is only as good as the company is strong, and if this outfit doesn't make it in the long term, you may have problems keeping it maintained and operational down the road.
Also, this kit you referenced comes with 11.4kW of PV, and 13kW of inverter capacity, and has 40kWh or battery capacity, or 32kWh or you keep to 80% DoD. The amount of PV is low for this inverter capacity, and for this amount of storage, in my opinion. This leads me to believe whoever put the kit together doesn't know much about off-grid design.
I would highly recommend you ask a lot of questions from the manufacturer before investing $40k on this equipment, and completely understand any limitations it may have. I would worry about inverter issues with phase imbalance, or with surge currents, etc. I don't see this system working out well for powering a whole house and garage, including EV charging and significant loads, without significant lifestyle changes needed during periods of low solar production due to weather and season.
A grid tie, net metered system would be far far less expensive and would not require lifestyle changes. Adding a backup battery for critical loads during outage would be a reasonably priced upgrade.
If you do go down this path, please provide updates here so we can learn from your experience. Good luck!