Solar, Battery, Generator, Utility combination
bmaclaff
TN
Licensed Electrician newby
I'm installing a 400A service with two 200A subpanels for a client. He wants a propane generator, solar panels, a battery bank and will be connected to the local power utility but does not want the solar to be grid tied. I know how to install daisy-chained automatic transfer switches for the generator (Generac ATS's are set up for this) but I'm looking for the best options for connecting all 4 sources. So far I've found that many vendors are generator only, some solar/battery only and some are low amperage only.
The design depends on what the client means by not having the solar tied to the grid. If they want a non-export system that works in parallel with the grid that's one design, if they want a PV+Gen+BESS system that only works as a backup power source when the grid is down that's a different design.
If you do not already have experience in this arena and have a list of products and part numbers and an idea of how it is going to be done in your mind already, I would not want you to take on this project. There are a lot of pitfalls and a lot of products to choose from and they don't all play well together, or work as advertised. Either that or throw a big learning curve price at the project. I've seen a number of these projects end up where the installer walked away with the project incomplete or incompletable because foundational steps were missed.
pv_n00b, yes a non-export system that works in parallel with the grid. I think the client's hope is to have the following priority- solar, battery, utility, propane generator in that order.
Birken, certainly good point. I'm doing the wiring on the job, that's settled. I don't mind getting extra expertice as needed. I agree with the concern about products not playing well together. I'm hoping to get an idea from those of you who know far more than I do, a good direction to go. I'd love it if I could find an ATS that could handle all or most of the options so that the solar array/inverter/batteries could be added later.
Not wanting for the solar to be grid tied and a non-export system that works in parallel with the grid are two different things.
What is the customer's goal:
  • Offset their energy use but not have to deal with an interconnect agreement?
  • Stick it to the man and not feed solar back to the grid, not matter what it costs them?
  • Minimize costs relative to some particular tariff structure?
People who try to "stick it to the man" with cleverly designed renewable energy systems often end up sticking it to themselves. :D
My 2 cents, which isn't worth even that much, is:
Any combination of 3 is easily accomplished, effective, and generally worth the cost.
Having a system with all 4 is a pretty useless endeavor in most, if not all, situations.
I'm going through this with a customer right now, and it's a bit of a disaster. I told them if they just want to offload money, it's a lot easier to take a big pile of it and light it on fire in their driveway. They have a partially installed solar system, an inverter, an MTS that needs to be changed to an ATS, no generator, and no BESS. I'm not sure why they want it all, for probably what will amount to 10 hours or less of utility outage a year, and yet here we are.
Solar with BESS and a generator to charge batteries when the sun is hiding is very common on off-grid sites, and there's a lot of them in my area.
Solar with battery and utility, whether you interconnect the solar or not, is very common, although non inter tied systems are pretty rare.
Like the others have said, it's important to find out what they are trying to accomplish before attempting to design the system.
Sounds like a micro-grid setup. From what I’ve seen, it’s usually easier to keep the generator on standard service-rated ATSs and let solar + batteries run behind a hybrid/off-grid inverter, instead of trying to find one box that handles all four sources at 400A. A lot of people split it into two 200A sections, or put PV/battery on one panel with selected loads. Just make sure the inverter has proper anti-islanding, since the solar isn’t grid-tied.
By the way, have you ever installed BYD Blade batteries for anyone? I saw a link https://cmxbattery.com/product/48v-...m-solar-home-battery-for-home-energy-storage/ claiming 10,000+ cycles, which surprised me. I always thought those were mainly for EVs , are they actually practical for home energy storage? Just curious.
thanks to everyone for input. To clarify, the client wants his solar system to be independent of the local power utility. sorry for unclear language on my part. I agree with the potential inefficiency of having this much redundancy. the location is fairly remote, which helps make the case. The rest of the rationale is simply the client's wish and he is willing to invest in his interests. He simply likes solar, but wants to ensure that if utility power is off that he will have the comfort of the propane generator if needed.
I did find at least one option (Tigo 200A MCB Auto Transfer Switch | Backup/Grid/Generator) that appears to coordinate all 4 but it remains to be seen if two of them can work with one generator. Peter-Lei's comment about separate solutions still may be the way to go though.
So what is the planned order of operation?
What will be the standard situation, house runs on utility power, solar does……? Keeps batteries topped off? What are the batteries doing? Are they configured like a UPS, and utility is running through them? Then what does solar do? Or are they unconnected until power failure and you need a ATS?
When does the generator come on, just to top off batteries? Will the battery bank be large enough to handle the entire load of the house, including peak demands, when utility is down, or will it need the generator also?
the hope is that the solar can power the house when possible, excess energy going into the batteries, switch to utility power when solar/battery not enough, switch to propane generator when all else fails. The client will want the largest solar array he can install. Battery bank size not decided yet. Yes it would be great if the propane generator topped off the batteries with excess when it is running.
This is obtainable, you need an energy management system that can control the output of the PV and battery and some strategically places CTs to monitor current flow. Then you can program it to reduce the PV output if it might export and the battery is full, this is just lost energy and money that the client will not be able to use but if that's what they want that's what they get. If the load is greater than the PV output then discharge the battery to reduce utility power used. Once the battery is discharged then use the utility power until the sun comes out. The generator can't be used when connected to the utility so it's not a factor in parallel mode.
If the utility drops then disconnect and run the PV+BESS+Gen as an islanded system. The key is a good energy management system that can control everything. This might lock you into using a particular vendor where the equipment all plays well together. Good luck.
There is about an infinite number of vendors for stuff like this now, it seems to change daily. Common is they are all from China and mostly geared toward DIY types or at least types that want to specify their own gear to the electrician. And in 5 years I predict that most of them will be out of business and leave you holding the bag.
Some thoughts based on poking at numbers for larger scale energy use but no professional focus in solar installations.
1) _Panels_ are cheap, batteries are expensive. Having a larger PV array and curtailing production (discarding energy that you don't use) will be cheaper over-all than having a perfectly sized array and using batteries to time shift the energy production around to when you need it.
2) Shifting energy use to match PV production (running power hungry loads when the sun is shining) is much cheaper than using batteries.
3) Residential energy use is _very_ peaky. You might 'need' a 400A service to handle peak loads, but only have an average power consumption of a couple of kW. If you are spending money on batteries and solar and the like, you might be able to reduce the utility service to the minimum (100A? less), and lean on your BESS system to provide for the peak power consumption. Of course if the BESS fails your utility fallback will be significantly limited. In this sort of use, you want to switch on utility power _before_ the batteries are fully depleted.
4) Batteries have a limited number of cycles and a limited number of years. For best battery economics, you want to use as many of those cycles as possible over the years the battery has.
5) Batteries are getting cheaper all the time. Make sure to give thought to more batteries in the future when they will be cheaper.
Traditional thinking says the voltage and chemistry of used batteries and new batteries even of the same type will not play well. So you might want to assume if upgrading batteries when cheaper that the original batteries will need to be disposed (hopefully sold to recover some value) rather than integrated into a larger system.