Solar Calculator for AC
Is there a good app or a special calculator for figuring AC calculations.
Example:70 KW system at 208 volts
I would like to go to sites and not have to add everything by memory
Thank You in advance
GoldDigger
Placerville, CA, USA
Retired PV System Designer
If what you do not want to have to remember is the formula itself, how about just writing your own spreadsheet with the right cells for inputs and use a spreadsheet app?
It is not all just adding. There is multiplication and division involved too. :)
Carultch
Massachusetts
Split Phase: Amps = Power / (Volts phase-to-neutral) / 2, assuming unity power factor.
Three Phase: Amps = Power / (Volts phase-to-neutral) / 3, assuming unity power factor.
In any case, make sure you check the datasheet, as the nominal power ratings can sometimes not match what you expect them to be.
jaggedben
Northern California
I would have said:
Split Phase: Amps = power/(volts line-line)
Three Phase: Amps = power/(volts line-line)/1.73
Same answer though. :)