Is there code specific wording on how to handle bus bar sizing for AC Combiner Panels?
I have a 800A MLO panel (with a 800A 100% rated breaker upstream) that collects the outputs of ten inverters (each rated for 72.2A continous current).
There are no loads on this panel, just power sources.
The output of this panel is what ties into the main switchboard (load side connection) and follows 705.12(B) for bus bar sizing etc.
Each inverter has a 100A breaker in this panelboard (total of 10).
My question is...does my 800A panelboard (AC Combiner Box) need to have an upsized bus bar akin to 705.12(B)? There are no loads and the max it will ever see is 722A of continuous current.
If I follow 705.12(B)(2)(3)(c) my bus bar is required to be 1000A which seems crazy to me since there are no loads. Am I missing something? Do I need to upsize? If not, where does the code support this approach?
Thanks! Long time follower, first time posting.
I have a 800A MLO panel (with a 800A 100% rated breaker upstream) that collects the outputs of ten inverters (each rated for 72.2A continous current).
There are no loads on this panel, just power sources.
The output of this panel is what ties into the main switchboard (load side connection) and follows 705.12(B) for bus bar sizing etc.
Each inverter has a 100A breaker in this panelboard (total of 10).
My question is...does my 800A panelboard (AC Combiner Box) need to have an upsized bus bar akin to 705.12(B)? There are no loads and the max it will ever see is 722A of continuous current.
If I follow 705.12(B)(2)(3)(c) my bus bar is required to be 1000A which seems crazy to me since there are no loads. Am I missing something? Do I need to upsize? If not, where does the code support this approach?
Thanks! Long time follower, first time posting.