Hmm good point, that is odd. Yes the ab inverter has always worked fine. Seems like they should have had the same issue assuming the programming was the same.What baffles me a bit is that you originally said the AB inverter(s) were working and only the BC wasn't. And I would have expected neither to work without reprogramming.
As we discussed in the last few replies, it is odd that it seems this was an issue for the inverter on the BC phase but not the ones on the AB phase.I apologize for not reading the whole thread, but I am catching up after a two week hiatus/vacation. As I understand it all the inverters are connected phase to phase, and earlier I asked if any of the inverters connected to the B phase had connections to the neutral. If they did, those inverters would see two different L-N waveforms 120 degrees apart with two different voltages; would this not be a problem?
Correct. And I am absolutely sure that the AB ones worked fine, and it was only the BC that didn't work. I swapped the inverters and everything. They all had a neutral connection. I did not have access to the grid code/parameter so it is possible those are different, but the solar contractor said they were all set the same (initially).As we discussed in the last few replies, it is odd that it seems this was an issue for the inverter on the BC phase but not the ones on the AB phase.
I see, but I would expect that any inverters connected to both the B phase and the neutral would be freaking out. Maybe some were and some were not?As we discussed in the last few replies, it is odd that it seems this was an issue for the inverter on the BC phase but not the ones on the AB phase.
Correct. Although I couldn't trace the conductors up to the pole transformer with 100% accuracy, it appeared the inverters had an issue with the open jaw but not the closed jaw.I see, but I would expect that any inverters connected to both the B phase and the neutral would be freaking out. Maybe some were and some were not?