I have solar edge.SE 43.kKUS has following string input from DC side:
1. 3 strings of 18 modules, 9 optimizers per string
2. 3 strings of 18 modules, 9 optimizers per string
3. 1 string of 17 modules, 9 optimizers per string
Optimizer used is P800P whose max ouput amps and volts is 18A, 85V.
Module power is 360W model SPR-X22-360-COM.
Inveter Spec SE43.2KUS says max input DC kw at STC/unit: 58.2kw/19.4kw
Question: I have total 63 optimizer whose max output power is 63x18x85 =96.39kW would that not exceed max input power 58.2kW inverter spec? Am I wrong?