ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
We recently installed an 812kW PV system on a hospital that has a big generator. The PV is connected in the MDP and there are numerous ATSs all over the hospital between the MDP and subpanels that are powered by the generator during a grid outage.That's what an automatic transfer switch is designed for. Put the ATS between the MDP and the protected loads panel with the generator on the PLP side and the solar on the other.