wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
The 2017 NEC (CEC) is silent on how to handle subfeed lugs. If you treat the MB of the panel supplied by the subfeed lugs as if it were a breaker in the panel (a reasonable approach, although not supported by any text in the NEC), then you are limited to a 70A breaker.electrical engineer didn't approve the method, so I could not use the lug kit method, he said the breaker in sub panel can be only 70A max. is this true? what if I use 400A load center with 200A main breaker.
That's because the only way to qualify the 200A bus shown in the service panel is with the 100% rule, and 125A + 70A < 200A. I think your PV may only need a 110A breaker? (100000*2*1.25/240 = 104A) Then you could instead use a 110A breaker for the PV and a 90A breaker in the subpanel. [Or, since the subfeed lugs aren't gaining you anything in this interpretation, a 90A breaker on the service panel bus.]
But it seems to me it would be much simpler to interconnect the PV via intercepting the 200A feeder to the subpanel not shown, leaving the bus and breakers in the service panel unchanged. The feeder interconnection rules are more flexible.
Cheers, Wayne