Solar panelboard

electro7

Senior Member
Location
Northern CA, US
Occupation
Electrician, Solar and Electrical Contractor
Was wondering if the attached panelboard could be rated at 225A instead of 400A. All the breakers are for inverters except the 20A, which is for the DAS system. Let me know your thoughts.
e79ee396f178e05229ef6fb0cf7a7a72.jpg


Sent from my SM-S918U using Tapatalk
 

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
I see people running up against this problem pretty often when trying to apply 705.12(B)(3). The sum of the PV CBs is 220A so a 225 A panelboard would be fine, but then there is that pesky load CB for something like DAS. I've seen people try to ignore that one. You have room for a 5A load CB. Does the DAS really need 20A? Can you power the DAS from another panelboard on site?
 

Carultch

Senior Member
Location
Massachusetts
I see people running up against this problem pretty often when trying to apply 705.12(B)(3). The sum of the PV CBs is 220A so a 225 A panelboard would be fine, but then there is that pesky load CB for something like DAS. I've seen people try to ignore that one. You have room for a 5A load CB. Does the DAS really need 20A? Can you power the DAS from another panelboard on site?
You can specify a 250A busbar. They are common in the 277/480V world.
 