Im just a low level electrician (and I dont understand the 50 + 50 = 87
, but I read the sum of all breakers code rule as "..shall not exceed THE BUSBAR..". In my interpretation I'd agree with Ggunn- that "busbar" would be referring to an individual busbar, i.e. phase A busbar. So if I had a three phase panelboard with three 3 pole breakers each 60A. And I had a 2 pole 20A breaker for a DAS on phase A-B and a 1 pole 20A breaker for carport lighting on phase C then I would be okay with a 200A rated panelboard/busbar. The sum of the breakers that are connected to each phase busbar would be 200A at that point, instead of adding all the breakers together for all three busbars which would be 220A. Would I be wrong in my interpretation?