1. We would like to receive a professional review for our design for a new solar plant that is under construction in California.
2. We have developed an engineering package , installation drawings that include the 48 VAC and communication feed to ~ 4000 heliostats , when no vehicles shall be driving and operators are not supposed to trip on the cables , we would like your opinion regarding compliance with NEC article 356.12 for LNFC conduit system .
3. The cable design includes a 22 gage and 10 gage cables , wrapped in a prefabricated cabling system in LNFC conduit , with plug connectors on each end for low labor cost installation, our design is to lay down the cables on the ground, we are dealing with ~ 120,000 ft of cables .
4. According what we see from the code, if we show that the cables are not subjected to a physical damage , we are in compliance to NEC code , we just need to verify that the cable and connectors are UL listed .
5. Therefore , we need a second written evaluation and approval that our design complies with the NEC code , we shall send our design after NDA and commercial approval .
6. As an option, we might ask you to support you in the presentation of our design with the final client.
2. We have developed an engineering package , installation drawings that include the 48 VAC and communication feed to ~ 4000 heliostats , when no vehicles shall be driving and operators are not supposed to trip on the cables , we would like your opinion regarding compliance with NEC article 356.12 for LNFC conduit system .
3. The cable design includes a 22 gage and 10 gage cables , wrapped in a prefabricated cabling system in LNFC conduit , with plug connectors on each end for low labor cost installation, our design is to lay down the cables on the ground, we are dealing with ~ 120,000 ft of cables .
4. According what we see from the code, if we show that the cables are not subjected to a physical damage , we are in compliance to NEC code , we just need to verify that the cable and connectors are UL listed .
5. Therefore , we need a second written evaluation and approval that our design complies with the NEC code , we shall send our design after NDA and commercial approval .
6. As an option, we might ask you to support you in the presentation of our design with the final client.