Meter-base adapters, that are inserted between the meter base and meter, have been available for a few years, providing a connection on the customer side of the meter for solar or vehicle chargers, without needing to find branch circuit space in the customer's main panels. While these may appear to avoid some costly main-panel expansions, do they meet all the NEC rules?
Most modern residential meter bases are rated 200 amperes, and most main panels have 200 ampere main breakers (that also serve as the service disconnect). The meter-base adapter adds another main breaker/service disconnect.
Most modern residential meter bases are rated 200 amperes, and most main panels have 200 ampere main breakers (that also serve as the service disconnect). The meter-base adapter adds another main breaker/service disconnect.
- the sum of the two separate service equipment overcurrent protective devices can now exceed the rating of the meter base. Is this permitted?
- the sum of the two separate service equipment overcurrent protective devices may exceed the rating of the service entrance cable, but this appears to be permitted by 230.90(A) Exception 3. Is using exception 3, allowing the sum of the over-current to exceed the rating of the service conductors, permitted?
- Would the provisioning of a second service disconnect, not grouped with the existing service disconnect be permitted?