That is incorrect. Terminal ratings do not affect the derating of conductors in a conduit. If you are using 90C rated wire then your derating can be based on 90C. You must also size the wire appropriately for the terminals, and the number of conductors in the conduit has nothing to do with that....
If I use 75° rating I can only place up to 9 conductors in a conduit, if 90° up to 20 conductors
Agreed. This is a common error, and I have encountered inspectors and plan reviewers who still don't get it.That is incorrect. Terminal ratings do not affect the derating of conductors in a conduit. If you are using 90C rated wire then your derating can be based on 90C. You must also size the wire appropriately for the terminals, and the number of conductors in the conduit has nothing to do with that.
I always assumed that Solaredge terminals had a 75 C rating and have never seen otherwise. I'm pretty doubtful they are 90C rated, just not 100% sure.
I think we're more concerned here with whether we can use 75C instead of 60C for termination. For AC as well as DC.Are there examples of installations with string inverters in which it would be a savings to be able to use the 90C rating of DC conductors if the termination ratings could be determined to be rated 90C?
Most inverter manufacturers don't document that their terminations are 75C rated? If so, 110.14(C) is very clear about the necessity of using the 60C termination ampacity unless 110.14(C)(1)(b) applies (>100A or >#1 AWG).Most inverter manufacturers just don't publish this information. When inverters have an AC circuit breaker you can usually get the terminal temperature for the CB.
I agree, but no one I know in the PV industry does this as it would require sizing a 90deg conductor like it was 60deg rated. Everyone just assumes the DC terminals are rated for 90deg and holds their nose. Luckily the DC string conductors are usually way oversized for the current anyway.Most inverter manufacturers don't document that their terminations are 75C rated? If so, 110.14(C) is very clear about the necessity of using the 60C termination ampacity unless 110.14(C)(1)(b) applies (>100A or >#1 AWG).
Cheers, Wayne
This is a bit wishy-washy, they won't say the terminals are rated for 75deg only that 75deg conductor or greater needs to be used. We can use 75deg conductor on 60deg rated terminals so the way they phrase it does not give the terminal temperature rating.The Solaredge HD Wave manual says to use only copper conductors with minimum 75C rating. That seems to fit the language of 110.14(C)(1)(3).
I don't. I assume and design for 75 degree terminals.I agree, but no one I know in the PV industry does this as it would require sizing a 90deg conductor like it was 60deg rated. Everyone just assumes the DC terminals are rated for 90deg and holds their nose.
No, not across the board. It gives four options, (a)(1) thru (a)(4). Using the 60C ampacity option is (2). This option allows you to comply without verifying anything else about the equipment, but it's only one option.Doesn't 110.14(C) state that the conductors rated at 100A or less can only use 60 degree Ampacity rating of the conductor size in 310.16?
Okay, true, but that means it neither requires or prohibits the use of any particular ampacity ratings from 310. Rather, it says the ampacity rating you can use depends on the terminal rating temperature, if the equipment being listed and 'identified for use' with such conductors....
The 110.14(C)(1)(3) talks about the temperature rating and not the ampacity rating.
Again, 110.114(C)(1)(a)(3) is the section. If the equipment instructions 'identify for use' with such conductors. *(Accidentally left out the '(a)' in previous replies.)Is there a section that states that we should be able to size the conductors for 75 and 90 degrees on 310.16