I agree 250.118 allows the use of a solid egc but I see that as being used in other than raceway. Where does it permit the use of solid wire for an egc that is larger than #10????? If this were a cable tray or other wireway that has hinged doors then you may be able to use solid egc.
What is the purpose of stating hat the use of solid wire larger than #10 is prohibited in raceways if you are going to say that 250.118 allows us. As far as I can tell you are saying there are no situations that an egc cannot be solid larger than #10. Basically you are saying that 310.3 should not exist.
What is the purpose of stating hat the use of solid wire larger than #10 is prohibited in raceways if you are going to say that 250.118 allows us. As far as I can tell you are saying there are no situations that an egc cannot be solid larger than #10. Basically you are saying that 310.3 should not exist.