Jim W in Tampa
Senior Member
- Location
- Tampa Florida
So are you saying we can use any color we want ?I disagree. No taping is required for a GEC.
So are you saying we can use any color we want ?I disagree. No taping is required for a GEC.
because it must be green or bare or reidentify with green tape if larger than #6
guess i been wasting green tapeJim, the GEC can be any color except for a color mentioned in article 200.
Roger
guess i been wasting green tape
IMO, It does not specifically say so. 250.62 says the GEC can be solid or stranded. It does not say it can be solid in conduit. Article 310.3 says it must be stranded in conduit for size 8 and larger.
250.62 tells you what can be used for GECs.
250.64 specifically says that the GEC can be installed in a conduit.
How does that not cover it?
I need alittle help in determining if the code will allow us to pull a solid #6 bare copper Grounding Electrode conductor inside a conduit with ungrounded and grounded current carrying conductors also inside of the same conduit? QUOTE]
Just for clarification what are the other conductors in the same conduit with the GEC
I need alittle help in determining if the code will allow us to pull a solid #6 bare copper Grounding Electrode conductor inside a conduit with ungrounded and grounded current carrying conductors also inside of the same conduit? The inspector says that this is a code violation and refers to Article 310.3, which states that any conductor #8 or larger inside a conduit must be stranded, the exception to this, states that except as permited elsewhere in the code. Article 250.62 states a Grounding Electrode conductor shall be copper, aluminum, or copper-clad aluminum, solid or stranded, insulated, covered or bare. Would this be an exception to a conductor having to be stranded in a conduit ? We know that you can put a grounding electrode conductor in a metal conduit for physical protection. Is there any other code references that would allow or disallow you to put a solid grounding electrode conductor #8 or larger inside a conduit? Do you agree or disagree with the inspector?
sell the bare #6 and buy some #6 green stranded. That and the savings in the labor will make up the price difference.
The wire does not need to be green.
I've never run a #6 GEC 100'.Not sure how far this is, but, if it's 100'+ my opinion would be: sell the bare #6 and buy some #6 green stranded. That and the savings in the labor will make up the price difference.
I have never driven rods more than a few feet away from the service equipment.Can you elaborate as to why?
I have never driven rods more than a few feet away from the service equipment.
Roger
DUH,
Slowly pulling foot out of mouth.
Just realized this is about a GEC and not an EGC. Never thought having the GEC in same conduit as the feeders, solid/bare/stranded/or otherwise. So didn't even pay attention to the "GEC" thingie when I read about pulling in same conduit:-(
guess i been wasting green tape
It doesn't hurt to use it just not necessary. I am sure some inspector will tell you it is necessary but it is not in the code book.
I've never run a #6 GEC 100'.
Roger
Can you elaborate as to why?
I have never driven rods more than a few feet away from the service equipment.
Roger
So you install a lot of small services on these buildings?You have never had to run all the way across a building to attach the GEC within 5 feet of where the water pipe enters the building? Happens all the time here when putting a new service in an existing building - especially commercial/retail buildings. Water is always coming from street and electricity always from alley and they enter on opposite sides of building.
So you install a lot of small services on these buildings?
Roger
Hence why I saidI assume you mean that since a # 6 GEC is being run it is a small service. To be truthful 20 years ago we still were running an occasional 100 amp service. Now a 200 amp usually goes in even if 100 amps would do the job. Although a 125 amp 120/208 three phase will deliver close to same amount of KVA as a 200 amp 120/240 single phase but that rarely is installed either.
I didn't say I have never run a GEC 100', as a matter of fact, I have run GEC's much further than 100'I've never run a #6 GEC 100'