Well, shoot! Thanks for all the replies even though it sounds like everyone thinks this thing will just burn up in the panel which is not what I wanted to hear.
When the SSR is on, it has a voltage drop of about 1.6V, so when the water heater is drawing current you will be dissipating about 30W at the SSR. If you mount the SSR on the side of the panel, and use the panel as a heat sink, then it will probably work. Mount a heat sink on the outside of the panel at the SSR location, and it will have an even better chance of working.
Unfortunately this becomes a design exercise rather than a no-brainer 'it will simply work'. Probably not what you want to sell your customer.
Something like https://www.automationdirect.com/ad..._ad-ssr2_-z-_ad-ssr6_series)/ad-ssr645-45-acz
would just barely fit in https://www.hammfg.com/part/1416E
This would handle the current and would not burn up, but now it is getting more expensive and taking up more space
-Jon