jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
It's right there in post #23.
Ya got me, I missed it. :ashamed1:
At least ya'll know where to find it in 2020 now.
It's right there in post #23.
We would plan our conduits accordingly and not "load them up", IOW's we would not have to derate the conductors to a lower ampacity than they are allowed at face value.
That translates to easy pulls even with solid conductors.
Roger
Ya got me, I missed it. :ashamed1:
At least ya'll know where to find it in 2020 now.
We haven't pulled solid copper conductors in decades except for when someone requires it in the spec. No one has ever given me a reason why it's better and IMO they cannot because it isn't. Especially today where everyone wants to value engineer down to the smallest possible size conduit packed to the max. We had a job several years ago where they specified #10 solid conductors, the wiring pulling crew had to fill some 1" EMT runs and needed a tugger to get the wire in. It pulled with so much force that it started to straighten out the offsets in the EMT. :slaphead: