Hi all,
I’ve inherited a set of 480 VAC industrial control panels that I’ve determined to be overdutied based on the previous engineer’s available fault current analysis (analysis performed after panel design and installation). For some reason as part of that analysis he did not also identify that the panels were overdutied as a result of the AFC. In these cases, the AFC is about 9.9 kA and the panels have elements that render it with the base 5 kA SCCR. These panels contain a number of motor control circuits, each with (in order from line to load) a manual motor starter, door-mounted disconnect for LOTO, PowerFlex VFD, Phoenix Contact 3-level motor terminal block, and motor. The door-mounted disconnect and VFD are the limiting factors. I’ve read every thread I can get my hands on in this forum about SCCR and have learned a tremendous amount, so I believe I can see what my options are, and I’d like some advice. As I can see it, I can either attempt to reduce the AFC to below 5 kA with an isolation transformer or replace the components in the panel that do not give me series combinations to get me above 10 kA. Both options have pros and cons:
I’ve inherited a set of 480 VAC industrial control panels that I’ve determined to be overdutied based on the previous engineer’s available fault current analysis (analysis performed after panel design and installation). For some reason as part of that analysis he did not also identify that the panels were overdutied as a result of the AFC. In these cases, the AFC is about 9.9 kA and the panels have elements that render it with the base 5 kA SCCR. These panels contain a number of motor control circuits, each with (in order from line to load) a manual motor starter, door-mounted disconnect for LOTO, PowerFlex VFD, Phoenix Contact 3-level motor terminal block, and motor. The door-mounted disconnect and VFD are the limiting factors. I’ve read every thread I can get my hands on in this forum about SCCR and have learned a tremendous amount, so I believe I can see what my options are, and I’d like some advice. As I can see it, I can either attempt to reduce the AFC to below 5 kA with an isolation transformer or replace the components in the panel that do not give me series combinations to get me above 10 kA. Both options have pros and cons:
- Isolation transformer: this would be the easiest to implement, in that it’s a single component to add, and would give me benefits of protecting the line from any harmonics from the VFDs, however I believe I’d be cutting it too close to the non-instantaneous trip region of the circuit breaker. The CB is 100 A and is comfortably in the range of instant trip with an arcing current of 6.5 kA (based on 9.9 kA bolted fault current), however unless I can very narrowly target 4-5 kA bolted fault current (3-4 kA arcing current), I may be too close for comfort to the non-instantaneous trip portion of the TCC, which would vastly increase my incident energy.
- Replace components: both the VFD and door-mounted disconnect have improved SCCR with class CC/J fuses, however there is not room for both the MMS and fuse holders, so I would need something like a Bussmann fuse block with disconnect switch to replace the MMS entirely and maintain the ability to disconnect individual motor circuits. I lose the thermal trip part of the MMS in that case, but as each motor is on a VFD I think the VFD would handle that fault protection. I wanted to avoid fuses but as I’ve learned it’s very difficult to achieve higher than 5 kA without fuses and the series combinations they enable. I’m also not seeing very many options for fuse holders with disconnect switches (at least of the DIN-rail mounted variety for use in a panel), which leads me to believe they are not widely used, which makes me second guess their application here.