Turned off when I arrived. Trips both the 50a branch and 100a main when turned on.
Turn on main with stove breaker off, no problem. Turn on the stove breaker, both trip.
Today's service call: Rental house has tripping breaker on electric stove. Go!
As before, please don't suggest a solution or step, then immediately demand the results. There's others on here that want to participate.
What happens when the stove is disconnected?
Something in the stove has shorted out. How old's the stove? Worth repairing?
Since just plugging in the stove pops the breaker (and I'm assuming it's with all of the knobs turned 'off')--
-- short in the power cord?
-- loose wire in the stove touching the frame (ie ground)?
Unplug stove: Breaker stays on.
As well as the 4-wire major-appliance circuit change. Years ago, a customer's son was badly shocked within a week of the lights and clock stopping working on their electric range. When I pulled the range from the wall, I found that the power cord went through a hole in the floor, instead of into a range receptacle.If anyone ever questions why you need a good ground you can show those pictures.
Or wrong or bent coverI wonder if someone replaced the studs on that?:
I found that the 3-wire range cord had been removed from the range, fed up from the crawl space, and re-installed without the cord clamp. I found that a single strand of each of the the stripped ends of the SE cable had been threaded through the holes of the prongs of the power cord and twisted around itself.
This was apparently done as part of a kitchen remodel that included relocating the range to a kitchen wall farther from the panel, and unfortunately for the son, closer to the sink. Inside the wiring compartment, the neutral conductor had pulled out of the crimped-on terminal, energizing the cabinet of the range.