1. Identify which of the receptacles, lights, or other loads are being supplied when either the #14 or the other "fighting" breaker (call it #M) are turned on.Time to leave breaker #14 off, attach a voltmeter to the terminal, then start turning off breakers 3,4,7,8,11,12,15,16,19 and 20. Whichever one turns off power to the terminal is the 'other side' of the dead short.
Now what?
Turn off all these loads, and then use a clamp meter to measure any current from #14 when it's turned ON to make sure that it's very low. If you can't make it near zero then note down the amount of current.
2. Put a high wattage lamp as Larry said (or another substantial test load) from the conductor fed by the #M breaker to the neutral bar (obviously with #14 and #M turned off. Then measure the current from the #14 breaker when it's turned on.
3. Starting at what you think might be the middle of the run to the loads noted above, open a box and if it has a hot wire feeding thru the box (ie., not dead-ending), put a clamp meter on the hot wire, and then turn on #14 to see if the load current is present. If no current then the short between the two circuits must be closer to the breaker panel, and so move to a box closer to the panel and check again. If current is present then move further away from panel. Try to zero in on location of "dead short", looking closely where you see hots are tied together. They can then be disconnected to check if the test load is no longer being fed, and further tests depending on what is found.
You measured 122.4V from the #14 breaker terminal to neutral when the breaker is turned off, so it's being back-fed by one of the phases. To determine which phase, measure the voltage at the turned off #14 breaker terminal relative to the busbar that feeds the #14 breaker (or relative to other "turned on" breaker outputs from that busbar). If you see about 240V then that confirms that the "other" circuit is on the opposite leg.Let's back up a bit. We know at this point there's two circuits tied together somewhere. But before we start on a wild goose chase, let's try to narrow down our search.
Breaker #14, which is a 15a, has 122.4v at the terminal when turned off. This means there's another circuit back-feeding into the panel. If it was a circuit on the same leg, then it would stay on and no breakers, even the main, would trip. But since the main trips, that means the 'other' circuit is on the other leg.
This means circuits 3,4,7,8,11,12,15,16,29 and 20 are suspects.
So I just used my voltmeter hooked to breaker 14 and.............?
and you got 120V at #14 with it off......?So I just used my voltmeter hooked to breaker 14 and.............?
~RJ~
I meant in series with the circuit line conductor. In other words, take wire off breaker, wire-nut it to one socket wire, put other socket wire on breaker.2. Put a high wattage lamp as Larry said (or another substantial test load) from the conductor fed by the #M breaker to the neutral bar (obviously with #14 and #M turned off.
I understood your post about putting it in series, but 480sparky's posts led me to believe that doing this might put 240V across the lamp if the breaker is turned ON. Hence my comment about putting the lamp between the line conductor on the breaker and neutral (i.e, about 120V), which should provide a test current through both of the circuits that are improperly tied together.I meant in series with the circuit line conductor. In other words, take wire off breaker, wire-nut it to one socket wire, put other socket wire on breaker.
Where were they joined at? Panel directory won't tell you that.
So cycling breakers 3,4,7,8,11,12,15,16,19 and 20 shows that turning off 11 turns off power to the terminal of breaker 14.
This means breakers 11 and 14 are tied together somewhere. But instead of opening boxes, I just read the panel directory.
14, as stated was "Kitchen hall bath basement lights". 11 is marked "Kitchen outlets".
They won't tell me which specific box... but they will give me an idea where to start looking.
14, as stated was "Kitchen hall bath basement lights". 11 is marked "Kitchen outlets". Now, where do you think those two circuits would share a box?
Never rely on the panel directory, try it as a search point yes but try not to believe it is true. breakers get moved, quick resolve disconnect # 14, no need for two feeds......
Dishwasher / Garbage Disposer almost always are the two kitchen circuits at common point. Although keep in mind the location of the nearest 14 circuit and the closest 11 circuit to one another is were I'd start, I at times put a little square of electrical tape on all the devices affected then look for a practical wiring path. almost always saves me hours.