Eddy_Current
- Canada
But, handle tie breakers should still be used rather than just sharing the neutral, if only for a safety consideration.. I mean, let’s say you are sharing a three phase circuit as three single phase live, one neutral, one ground, each phase on its own as far as outlets are concerned as all equipment is on 120 volts... even if you run a larger neutral and a larger ground than the live wires, there is still the potential of overload through heating of the neutral or of a fault that trips the one phase still allowing current on the neutral thus still faulting on the other phases but not tripping...
so, how do you account for it? With a sign that says if breaker x is tripped y and z need turned off to work on circuit?
Would rather a handle tie at least... and I am one of those they call a handyman who is studying code.. I think I am qualified to do a lot of electrical but this forum has taught me that I have a lot of learning to do...
I agree for safety they should be tied, but they don’t have to be and rarely is done. No labeling required. We are used to it and know to look for it.
For instance, in most commercial buildings they will have three circuits for lighting, all sharing a neutral on three single pole breakers. At 347 volts you can put many lights on one 15 amp circuit so when you turn off one of them, it could turn off all the lights on half of the floor. Then if you get into the junction box assuming power is off but there still is potential danger working on the neutral supplying the other two circuits.