Hey all,
I have inherited a "new to me" problem.
I have a new house ($2.5M) that's coming to completion/final that I have been called out to take over the Burglar/Fire (combo) alarm system install which is roughed in and panels are up.
I do this for a living and have not encountered this issue before.
Upon further inspection I found a "fire wire" (18/4 FPL) in the mix. When I approached the "old alarm company installer" he stated that yes he has pulled a fire wire from the panel to each detector in a row to the last detector. I said I didn't see any of "our smokes" on the job and he said "nope I used the new LV/HV smokes and did it with the electrician!"
I thought to myself, wait WHAT??
I hadn't seen a dual use smoke yet, and I immediately started thinking separation etc.
These are ESL 350CC smokes. They are not approved by GE for this use (says so in the instructions and confirmed with w quick call to GE tech). They are wired and installed (in tandem on the 125vac side) and connected together correctly to the Form-C (if you could actually do this) on the 12VDC side.
I know I shouldn't even touch this - but their up and customer will explode if there's one more issue out there. My common sense says don't - but even GE said some people have done it that way, its just not supported/approved, period! (thats almost enough for me - I will not add additional liability to my side if I can help it)
What do you guys think, have you ran into this before?
Wouldn't there need to be something separating the two?? Even if both wires are rated at 600v (the site electrician's boss said it was OK)?
Any ideas/thoughts would be appreciated (or even an idea on how to spring it on the old installer (friend) and or homeowner:wink: ), I cant just walk...
Jim
I have inherited a "new to me" problem.
I have a new house ($2.5M) that's coming to completion/final that I have been called out to take over the Burglar/Fire (combo) alarm system install which is roughed in and panels are up.
I do this for a living and have not encountered this issue before.
Upon further inspection I found a "fire wire" (18/4 FPL) in the mix. When I approached the "old alarm company installer" he stated that yes he has pulled a fire wire from the panel to each detector in a row to the last detector. I said I didn't see any of "our smokes" on the job and he said "nope I used the new LV/HV smokes and did it with the electrician!"
I thought to myself, wait WHAT??
I hadn't seen a dual use smoke yet, and I immediately started thinking separation etc.
These are ESL 350CC smokes. They are not approved by GE for this use (says so in the instructions and confirmed with w quick call to GE tech). They are wired and installed (in tandem on the 125vac side) and connected together correctly to the Form-C (if you could actually do this) on the 12VDC side.
I know I shouldn't even touch this - but their up and customer will explode if there's one more issue out there. My common sense says don't - but even GE said some people have done it that way, its just not supported/approved, period! (thats almost enough for me - I will not add additional liability to my side if I can help it)
What do you guys think, have you ran into this before?
Wouldn't there need to be something separating the two?? Even if both wires are rated at 600v (the site electrician's boss said it was OK)?
Any ideas/thoughts would be appreciated (or even an idea on how to spring it on the old installer (friend) and or homeowner:wink: ), I cant just walk...
Jim