Something I ran into...

Merry Christmas
Status
Not open for further replies.

jason

Senior Member
Location
Georgia
Someone fed a 100 amp subpanel with a 6/3 and an 8/3 copper paralleled. These were protected (or not) by a 100 amp breaker. This is not part of the job I'm there to do, but it may be serious enough to fix regardless. I haven't mentioned it to the homeowner yet. This is a residence. However, it got me wondering. Lets say the load was 60 amps. How would the current be distributed on each wire? 30/30 40/20 60/0 ??? I have no idea and I know it's not right, just wondering.
 
jason said:
Lets say the load was 60 amps. How would the current be distributed on each wire? 30/30 40/20 60/0 ??? I have no idea and I know it's not right, just wondering.

The conductor size will not limit current - so 30/30...
 
iwire said:
Whoa, of course the conductor size will have an impact on the current split. :smile:

In a fault condition yes... Under a 60a load not by much, certainly not 40/20.... Doubt 1a could be measured in difference under a moderate load.
 
stickboy1375 said:
I find it interesting that someone would run two feeders vs 1 correctly sized feeder, I would love to know the whole story on this one...

I don't know either but it looks like it'll be a pain feeding a #2 into that panel. The panel is on an outside wall that a joist runs right beside. I was wiring a spa and caught hell fishing the 6/3 to it. Luckily there was a spare 10/2 that I could tie on to.
 
jason said:
I don't know either but it looks like it'll be a pain feeding a #2 into that panel. The panel is on an outside wall that a joist runs right beside. I was wiring a spa and caught hell fishing the 6/3 to it. Luckily there was a spare 10/2 that I could tie on to.

Do a load calc and see if you can just eliminate the 8-3...
 
stickboy1375 said:
I'm also going to assume they doubled up the lugs on both ends as well...

Ok, although it's really crazy, let me clarify. This is what it is. A 100 amp QO breaker in the main panel. Using a reducer/splicer, they put the #6 and the #8 on one side and a #2 at the other side and going to the breaker. Then once under the house they put a junction box and also spliced just as they did in the panel to a #2 and went to the sub panel from there. So the sub panel has 40' of #2 SER going to it, just as you'd expect.

Maybe this was to fool the home owner?
 
jason said:
Ok, although it's really crazy, let me clarify. This is what it is. A 100 amp QO breaker in the main panel. Using a reducer/splicer, they put the #6 and the #8 on one side and a #2 at the other side and going to the breaker. Then once under the house they put a junction box and also spliced just as they did in the panel to a #2 and went to the sub panel from there. So the sub panel has 40' of #2 SER going to it, just as you'd expect.

Maybe this was to fool the home owner?

Using up left over material? :confused: Wow, hey just so you know #2 ser is only good for 90 amps...
 
Percent difference.

Percent difference.

iwire said:
I don't know by how much but I agree 40/20 seems imposable.
1000' of #8 has .8 ohms resistance
1000' of #6 has .5 ohms resistance

.8-.5=.3
.3?.8=.375 or 37.5% difference in resistance.

That sound right?
 
stickboy1375 said:
Using up left over material? :confused: Wow, hey just so you know #2 ser is only good for 90 amps...

Not as a sub feed. 100 amps if supplying a sub panel, right? I've done this hundreds of times and have never had it turned down.
 
jason said:
Not as a sub feed. 100 amps if supplying a sub panel, right? I've done this hundreds of times and have never had it turned down.

Your trying to use table310.15(B)(6)... this table is only for the "main power feeder", so 100 amps if its a dwelling service, 90 amps for a sub-panel.
 
stickboy1375 said:
Your trying to use table310.15(B)(6)... this table is only for the "main power feeder", so 100 amps if its a dwelling service, 90 amps for a sub-panel.

Thanks. Lots of improper sub panels out there.
 
jason said:
Thanks. Lots of improper sub panels out there.

Yes, all over the place, the NEC has been changing the wording of the section to try to clear up the confusion.

Only the conductors that supply 100% of the dwelling units power can be sized using table 310.15(B)(6).
 