No strikeouts here guys...Except maybe on my part. I just really appreciate a second set of "eyes" on this issue. One of the things I should refresh memories on here is that there is a second TV and converter set on its own coax run that is also sending about 42 volts back to the outside splitter. It is on separate circuit. The circuits involved feeding the TV's are the same phase. Lets say they are circuits 10 and 14. The cable splitter at the point of entry to the home is bonded to the service riser with a # 10 solid copper. I did a load test at the service panel to see how the voltages reacted. I applied a 120 volt load (microwave) and a 240 volt load dryer. Voltages at the panel remained solid during load test (each phase to ground and phase to phase). So, if there was a loose neutral, there would have to be several downstream neutral connections loose, as each TV setup (each has its own circuit) introduces voltage back on to the coax, and I even temped up a separate circuit from an extension cord from a third circuit to feed one set with the same results of voltage going back to the coax entry point. The TV cords are OEM and are not grounding types, just two prong. Same with the converter boxes.