When you have a large PV array (with no optimizers), and you have multiple combiners going to a recombiner, and the recombiner output goes to the inverter... are the wires between the multiple combiners and the recombiner considered source or output circuits? I am assuming they are considered output circuits.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
They are output circuits. A source circuit contains only solar modules in series. Once it's paralleled to another circuit or connected to another device it becomes something else.

One could argue that source circuits are a subset of output circuits, but I'm not sure it makes a meaningful difference to anything.
 

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
Get ready for the 2023 NEC where it looks like they are doing away with the concept of source and output circuits.
 