Coppersmith
- Tampa, FL, USA
- Electrical Contractor
My client purchased a spa and asked me to put in a circuit for it. He showed me all the documentation for it and there was nothing about the breaker size although he said they told him 60 amp @ 240v. Wanting to verify, I called the seller and a grouchy lady barked it was 60 amps. I said I thought that was a bit high and could she verify. She called someone on the manufacturing floor and they said 50 amps. I waited until the spa arrived before purchasing an expensive 2 pole QO GFCI breaker (that may not be returnable) because this all sounded fishy.
The spa arrived and I looked for a nameplate with the required data. A sticker on the control box (where it gets wired) said 240v/60hz/40A. This is the only electrical data attached to the spa. I installed a 40 amp GFCI breaker and told my client the spa seller didn't seem to care too much about his safety.
Apparently my client called to complain and they sent him a page from some manual they never included with the sale that says if the "total amperage rating of the power system is 36 to 40 amp" then the GFCI breaker size should be "50 amps".
Does this seem right? I'm thinking 40 amps is still the correct size because the label says 40 amps. I measured amp readings averaging 35 amps with short spikes in the low 40's. (This is the spa heating up for the first time.) The breaker hasn't tripped so far. What say you experts?