Does the feed for an externally mounted spa box need to be in conduit? Is that a 2005 requirement or is it in the 2002?
Thank you.
Thank you.
No, but 680.42(C) does.Originally posted by jjhoward:
Does 680.21(A)(4) allow cable to be run from the main breaker panel in the one-family house to the location on the inside wall where I will pass through to the exterior mounted spa box?
Yeah, I saw my first post again after I posted, and realized my goof.Originally posted by jwelectric:
George
Nice try from memory but a little short unless you meant ... 680.42 (C) Interior Wiring to Outdoor Installations.
That's one of the questions that I've asked myself many times. In my area, they permit NM for this, despite what 680.25 seems to say. I don't know what the special hazard is that this section is trying to mitigate.Originally posted by jjhoward:
Looks like 680.25 dictates conduit.
Why must the feeders for a spa or a pool be run in conduit IN an unfinished basement? Is there some safety issue here? Sure, conduit outdoors but inside too? Are jboxes and splices too risky for pools and spas?