Stubbie said:
Anybody know if there is a code reference addressing extending a 20 amp branch circuit to other structures (specifically a shed) from a spa panel (hot tub outdoors) disconnect that has two slots for circuit breakers besides the gfci? I keep thinking I have seen an exception that prohibits doing any branch circuits to other than spa equipment. Reason for asking is the use of the spa panel will allow 75 feet to be erased for the run to the shed.
stubbie
If I understand your question correctly, then yes, there are a few code references.
Starting out with 680.42. This states for an outdoor installation of a Spa or Hot Tub you must comply with Parts I and II of article 680 that would otherwise apply to pools installed outdoors.
Then progress to 680.25 (B) (2), which states you can use the feeder to a separate building (in this case the shed) to also supply swimming pool equipment branch circuits, if you follow the grounding requirements also listed in 680.25 (B) (2).
I know a Spa is not a pool, but the interpretation from 680.42 is that you would otherwise treat the Spa installation as a pool installed outdoors. SOME JURISDICTIONS MAY NOT USE THAT SAME INTERPRETATION.
Now, you are wanting to use a 20 amp branch circuit from the Spa panel to the shed. Obviously that could not be the feeder that is supplying the spa panel, so it would not meet the requirements. You need to figure out how to continue the original feeder (from the power source to the spa panel) on to the shed. Perhaps a splice in the spa panel, tapping to feed the spa panel and continuing to the shed and setting a 2-space disco in the shed.
If that is clear as mud, I have done my job and it's time to mosey on into the sunset for this day...........:grin: .