- Location
- Currently in NJ
I was looking over a Connecticut Electric spa panel and noticed not a gfci breaker but instead just a blank faced gfci, the pull out and 15a breaker. I opened it up and saw that the line comes in and is routed through a ct which is mounted/integral to the gfci, then into a four pole contactor. One of the feeders has a jumper that goes to it's own pole of the contactor which then feeds the 15a breaker. My question is, if the spa is running and there is a load on the 15a breaker the gfci should trip but I must be mistaken otherwise the setup wouldn't work under such a condition which it was manufactured for.
	
		
			
		
		
	
				
			 
				
 
 
		 
 
		