I swear there is a code requirement which does not allow a new hot tub/spa to be served from a sub-panel. Am I making this up, or can someone point me to the right place...?
Thx
Thx
Boy, our references are all over today.
(1) Feeders. Feeders shall be installed in rigid metal conduit or intermediate metal conduit. The following wiring methods shall be permitted if not subject to physical damage:
(1) Liquidtight flexible nonmetallic conduit
(2) Rigid polyvinyl chloride conduit
(3) Reinforced thermosetting resin conduit
(4) Electrical metallic tubing where installed on or within a building
(5) Electrical nonmetallic tubing where installed within a building
(6) Type MC cable where installed within a building and if not subject to corrosive environment
Exception: An existing feeder between an existing remote panelboard and service equipment shall be permitted to run in flexible metal conduit or an approved cable assembly that includes an equipment grounding conductor within its outer sheath. The equipment grounding conductor shall comply
with 250.24(A)(5).
(2) Aluminum Conduit. Aluminum conduit shall not be permitted in the pool area where subject to corrosion.
(B) Grounding. An equipment grounding conductor shall be installed with the feeder conductors between the grounding terminal of the pool equipment panelboard and the grounding terminal of the applicable service equipment or
source of a separately derived system. For other than (1) existing feeders covered in 680.25(A), exception, or (2) feeders to separate buildings that do not utilize an insulated equipment grounding conductor in accordance with 680.25(B)(2), this equipment grounding conductor shall be insulated.
I don't know why I'm thinking this. Now I wonder if it was a specific local AHJ req'mt.