LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
My bad; you're right. #6 or smaller. D-oh!Actually, it's smaller than #4.
My bad; you're right. #6 or smaller. D-oh!Actually, it's smaller than #4.
Fo shoDon't forget that smaller than #6 must be white, not re-colored white.
Did they tell you that you could use #8 for 50 amps?I called the manufacture. I am good with #6 after the sub/gfci.![]()
That's just for from disco to tub.Don't we need a copper EGC here? Or is that just for the branch circuit?
No, the spa manual requires #6 for a 50 amp’s first 100’ and #8 for 40 amp’s first 100’.Did they tell you that you could use #8 for 50 amps?