Anything else I should be thinking about?
If the entire run is outdoors, consider PVC and conduit and individual wires for the whole thing. Some of the reasons are, in no particular order:
UF is a pain to pull in PVC, probably the most difficult of any wire pull.
You're supposed to size conduit as if the cable's width is its diameter.
Individual wires should cost less, plus cost saving with smaller conduit.
Another cable option from the panel to the disco is SER, also good if you're feeding a sub-panel rather than a single disconnect. All things considered, I'd go for the PVC with copper conductors.
I think of UF as the best cable to use when there will be no conduit, either exposed (but protected from damage) or underground. Otherwise, it's basically just a pain-to-use variation of NM cable.