It wouldn't need that. I know its divided the forum before but the insulated EGC is only required for pool feeders not packaged spas and also required for the wiring that goes from the disconnect to the spa. Any chapter 3 wiring method is allowed to the disconnect of a packaged spa.
I guess I'm still part of the division.
Article 680 indicates Swimming Pools, Fountains and Similar Installations.
Hot tubs and Spas are in the list.
680.7 (A) specifically indicates feeders and branch circuits installed in a corrosive environment "or wet location" shall contain and EGC that is insulated copper conductor sized in accordance to Table 250.122 but no smaller than 12 ga.
To me if it's an "underground feed" (whether that be a feeder to the disconnect, or the branch circuit to the spa), then it's considered a "wet" location and would require an insulated EGC.
I don't consider the "bare" ground in UF as an insulated EGC.
If it were insulated, we probably wouldn't refer to it as a "bare" equipment grounding conductor.
Now, of it's a feeder to the disconnect or branch circuit that is "not" installed in a wet location I would think UF with a bare EGC would be fine.
JMHO.
Jap>