ramsy
NoFixNoPay Electric
- LA basin, CA
- Service Electrician 2020 NEC
It appears 680 does not apply if raceways are > 5ft from pool / hot tub?IMO, the wiring method mentioned in 680.11 includes the feeder.
It wouldn't need that. I know its divided the forum before but the insulated EGC is only required for pool feeders not packaged spas and also required for the wiring that goes from the disconnect to the spa. Any chapter 3 wiring method is allowed to the disconnect of a packaged spa.
A factory assembly of one or more insulated conductors with an internal or overallInsulated copper conductor means it has insulation around it. I don't know if the pour around the UF would be considered insulated in the eyes of the NEC
"Covering"
Of nonmetalic material suitable for direct burial in the earth.
My point was you and Jap considering the eguipment ground in uf cable not insulated but covered matches the definition of uf cable.Your point? One or more-- it doesn't say all conductors are insulated-. It appears to me that the egc is not considered insulated
Now look at art 100 and see difference between insulated and covered.Yes but the insulated part can be in a cable sheath still.
And ya I should've prefaced dwelling units too since I made a blanket statement
All metal parts required to be bonded by this section shall be bonded together using a solid copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG.
Other than listed low-voltage luminaires not requiring grounding, all through-wall lighting assemblies, wet-niche, dry-niche, or no-niche luminaires shall be connected to an insulated copper equipment grounding conductor installed with the circuit conductors.