hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 10kva 208V three phase unit space heater. This is Not baseboard heater and its mounted on ceiling.
One dedicated branch circuit breaker size to the unit heater provided is 40A with 3#8 + 1#10G branch circuit cable size.
I cited NEC 2014 section 424.3 breaker size too big but I got response that 40A with #8 cable size is in compliance with 424.3.
I am not sure is 40A breaker size with #8 cable size for 10kva 208V three phase unit heater in compliance with 424.3 or not? What are your thoughts?