Re: Spacers?
I?m a bit late getting into this one, but that has never stopped me from engaging in a discussion of physics. I have always believed that the purpose of maintaining spacing in underground runs was to maintain a constant impedance throughout the length of a run, and thereby to prevent the occurrence of hot spots. Here is what I mean:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Any single conductor in isolation has a value of resistance and a value of self-inductance. If it is close to no other conductor, and is far enough from planet Earth, it will not possess the property of capacitance.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Any set of two or more conductors in proximity to each other or in proximity to planet Earth will possess the following properties: Each conductor has resistance and self-inductance, and any combination of two conductors will have mutual inductance and capacitance.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">All of these properties can be measured on a ?per unit of distance? basis.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">If the spacing between conductors in held constant, then the values of all impedances (resistance, inductance, and capacitance) will maintain a constant value on that ?per unit of distance? basis. Therefore, any heating that takes place along the length of the run will have the same impact on each linear foot of conductor along the entire run. There will be no hot spots. Please note that this will be true whether the conduits are one millimeter apart for the whole run, or 30 feet apart for the whole run. Distance of separation is not relevant here, only that the distance remain constant.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Now suppose you have two conduits in a long run. Suppose they are nearly in contact with each other for some distance, then they are separated by a foot or so for some distance, then they are close to each other for some more distance, and throughout the run the distance between the conduits varies randomly.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">In this case, the values of impedances (inductance, and capacitance, but not resistance), as measured on a ?per unit of distance? basis, will vary throughout the run. That is because the values of mutual inductance and capacitance depend on the distance between the two conductors. The current flowing will be based on the supplied voltage and the total effective impedance. But the heating that takes place along the length of the run will depend on the impedance in the local area. As a result, some portions of the run will experience a greater amount of heating then other portions.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">The danger here is that a run with properly selected overcurrent protection can still be at risk of hot spots that lead to insulation breakdown, eventually resulting in a ground fault, without the total current ever exceeding the breaker's trip point.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">I think that this discussion does apply to any installation, but the actual differences in heating effect will depend on the voltage and current levels. It is probably insignificant below 4160 volts, and would probably not the installation that Lady Sparks Lover has described. That notwithstanding, I believe that this is the reason for the code requirements for maintaining spacing.