I agree that there is no contradiction, but my reasons are different. Part (a) says you can?t put any foreign piping in the ?dedicated space.? But that term means the space defined by the footprint of the equipment, extending 6 feet above the equipment. Once you are 6 foot 1 inch above the equipment, you are no longer in the ?dedicated space.? Part (b) talks about that area, the area more than 6 feet above the equipment. You can put a pipe there, but only if you put drip-protection.