hacim23
Journeyman Electrician
- Location
- washington, DC
- Occupation
- Electrician
On the job I've typically heard 1/2 inch spacing between uninsulated parts up to 1000v. For the most part I haven't seen anything that close except for some ATS' that come equipped with lugs and the spacing between some of them is barely enough to get a finger between. The ATS has an arc shield that goes between phases but does not completely isolate everything. We have wrapped (fish-paper) around B phase just to be safe but I also know that we haven't on some of them and had no issues. Is this covered in the NEC or is there something more specific to an ATS? This example is 400A, 480V. Thanks.