If i have spare cables not feeding any load fed from panelboard feeder breaker then they must terminate in junction box? I cant find correct section in NEC 2017
If they're not energized then a junction box is not necessary.
Why would anyone want to do that???What if they are energized but not feeding anything?
Why would anyone want to do that???
I would find a reason to hang a red tag, even if I have to make something up.Spare future use who know
Agree 100% but if the load end is in a J box and they are taped or wire nutted I don't think it is a violation.I would find a reason to hang a red tag, even if I have to make something up.
Connecting conductors to a power source, with nothing connected at the other end is just asking for an accident to happen.
I was always taught that the very last connection made to a circuit is to the power source. You only do that after everything else is connected.
Agree 100% but if the load end is in a J box and they are taped or wire nutted I don't think it is a violation.
Where is the code section NEC 2017 for this?
There isn't one as far as I knowWhere is the code section NEC 2017 for this?
If they are capped or terminated in a box, it would not be a violation, but I would try very strongly to convince them to determ the conductors at the breaker.Agree 100% but if the load end is in a J box and they are taped or wire nutted I don't think it is a violation.
I think it could be considered an outlet even if it is not connected to anything.There isn't one as far as I know
Actually 300.18A requires the conduit run to be complete prior to installation of the conductors. 300.15 requires a box for termination of conductors. I consider this the references to require what the OP is asking.There isn't one as far as I know
Here's another one: What code section requires me to use insulated conductors in conduit?
What if they are energized but not feeding anything?