I have a situation where we are removing some 480V equipment (4/0 conductors) the owner wants the cables removed to an adjacent j-box as a emergency just in case ckt. or for future use. With the availability of someone accidentally energizing the feeder what are some percusations to take in order to insulate the conductor in the pull box is taping adequate of is there some kind of ?boot? 600V class I could utilize? Unless someone makes a wirenut for a 4/0 conductor..
 

celtic

Senior Member
Location
NJ
Remove them from the breaker.....heat shrink a cap over both ends [tape would work just as well]...tag both ends.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
William1978 said:
Try a polaris block that should work.

I agree, or a 2 hole insulated tap would work well. You'll be ready to hook right onto it should you ever need those wires.
 
Last edited:

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Mike01 said:
I have a situation where we are removing some 480V equipment (4/0 conductors) the owner wants the cables removed to an adjacent j-box as a emergency just in case ckt. or for future use. With the availability of someone accidentally energizing the feeder what are some percusations to take in order to insulate the conductor in the pull box is taping adequate of is there some kind of ?boot? 600V class I could utilize? Unless someone makes a wirenut for a 4/0 conductor..
if they are in an adjacent jbox how would they get energized?
 