Jhunter1313
- San Diego, CA
So, I have some highbays in a warehouse, that were originally unswitched (wire went straight from the breaker to the lights), and they have been working fine. The customer now wants to be able to switch the lights. So I ran a series of contractors and a time clock/switch, re-routed the wires from the panel to go from breaker to contactor, then contactor to lights.
Jumping off of one of the highbay line sides of the contactors, I brought power to my time clock/switch.
When I turned everything back on, the time clock/switch did not turn on, even though power was present.
I checked voltage on all the line sides of my contactor points (10 spots in total) and each one of them produces a small little spark where my multi-meter lead touches the ground screw....and i am not understanding why.
A little more background info in case it helps:
The voltage is 277;
Each breaker is a 2-pole breaker, one pole is the switched line, the other is the emergency circuit that goes straight to the EM lights;
The time clock/switch is jumping off of one of the breakers, and then switch legs out to hit each contactor coil (3 of the contractors are about a foot away from the switch, the last one is about 500' away at the other end of the warehouse, where it hits just the coils of the 4th contactor);
The 4th contactor is powered by the time clock/switch, but the circuits it passes through are from a different panel (still the same exact scenario...2-pole 277v, etc);
I have a ground going through every conduit and raceway, and is terminated and/or grounded in every junction point;
Going through the chase nipple from the original panel to the contactor box, I have about 22 wires (10 hot wires from breaker to contactor, 10 hot wires from contactor to the lights, a neutral going from contactor coil to panel neutral bar, and a ground, tied in with the other grounds, and landed on ground bar in the panel).
The voltage is 277;